I am involved in a project in which an existing building is being stripped and renovated in its entirety. Its incoming utility service is 480V, corner-grounded delta.

As the project is presently designed, we are stepping this down to 208/120Y and serving all of the building's loads via the 208/120V distribution system. Aside from serving the step-down transformer, the 480V side is mostly going unused. The size of the step-down transformer is increasingly becoming an issue, as the existing electrical room can only accommodate so much equipment. I am considering shifting some loads (A new elevator and some new HVAC equipment, in particular) to the 480V side of the distribution system, but I have some concerns.

I know that a typical three-phase load with a rated voltage doesn't "care" whether a voltage is line-to-line or line-to-neutral, so long as the voltage's value is correct. But what about equipment involving the use of VFDs, soft starters, and solid-state electronics? Is it safe to serve such equipment from a 480V, corner-grounded delta system? Or does a possibility exist that some component is going to be expecting a reduced line-to-neutral voltage, as would be the case in a Y-connected system?

Are there any other potential issues that I may not be considering?
 
Replies continue below

Recommended for you

Oh whew. Center grounded delta. This was a 277/480 system. All the lights in the place are 277V.

Couldn't get near that with a slash rated 480V breaker.

Keith Cress
kcress -
 
My mistake. I saw "center Grounded" and assumed "center grounded delta" once again proving the adage that when you/I "Ass U Me"....

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 