FlaBouy
Electrical
- May 30, 2007
- 2
Hi guys, new member here. Can someone explain how one figures breaker size/fixture quantity for 480V single phase 1000W metal halide fixtures on a three phase feeder utilizing a 3 pole contactor fed with a 3 pole 480V breaker. Switching is via 120V control. I understand balancing single phase loads (A,B... B,C... A,C) to the contactor, just a little confused at how you determine maximum amount of 1000W fixture on a 30A breaker.
I assume that at 2.4A per fixture I am allowed 10 fixtures per single phase circuit to meet a single phase continuous load (30A x .8 = 24A)But say this is a three phase breaker/contactor... How do you calculate that same 30A circuit...
Thanks
I assume that at 2.4A per fixture I am allowed 10 fixtures per single phase circuit to meet a single phase continuous load (30A x .8 = 24A)But say this is a three phase breaker/contactor... How do you calculate that same 30A circuit...
Thanks