lefty51
Electrical
- Jul 9, 2008
- 33
Received a call today from maintenance. They are going to be hooking up an convection heater. Rating is 55 FLA.
On the front of the panel, it states " short circuit amps - 5KA - symetrical ". Inspector mentioned something to one of the maintenance personnel, that we may have to install a transformer to reduce this?? The feed is fed from an MCC with HRC fuses - IR capacity of 200KA. Why would be need to install a transformer ? There is the main feed from the MCC ( fused ) , then a main switch at the unit itself.... and also fuses inside the console. Am I missing something here. If the unit is capable of putting out 5KA under short circuit conditions, but the fuses are capable of interuppting more than 5 KA, then there should not be a problem..correct ? Possibly the maintenance person got his wires crossed...????
On the front of the panel, it states " short circuit amps - 5KA - symetrical ". Inspector mentioned something to one of the maintenance personnel, that we may have to install a transformer to reduce this?? The feed is fed from an MCC with HRC fuses - IR capacity of 200KA. Why would be need to install a transformer ? There is the main feed from the MCC ( fused ) , then a main switch at the unit itself.... and also fuses inside the console. Am I missing something here. If the unit is capable of putting out 5KA under short circuit conditions, but the fuses are capable of interuppting more than 5 KA, then there should not be a problem..correct ? Possibly the maintenance person got his wires crossed...????