unclebob
Electrical
- Sep 16, 2004
- 350
What happens if you try to use a 500 hp motor, rated at 440 V , with a 6-pulse drive, rated at 600 A?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
“6 pulse drive” is a clue that this is AC…Hmm. I see a lot of assumptions being made here. The original post did not mention whether the machine was AC or DC - in which case a 440 V(dc) design could be fairly recent manufacture, for a very specific application and/or installation. Also - OP did not mention a nameplate current or speed: a typical three-phase AC machine would be drawing in the neighborhood of 580 A at 440 V; a comparable DC unit would draw around 890 A. A 600 A(ac) drive might have enough to run flat out ... a 600 A(dc) drive won't.
If it IS an older machine (AC or DC), the concern for winding damage from the electrical stresses occurring due to the drive output voltage waveform is valid. Additional thermal stress from the harmonics being produced in the drive output current waveform will also accelerate failure.
Had the OP mentioned 460 Volts (standard motor voltage rating) rather than the very old 440 Volt rating, that would not change the 480 Volts standard North American Source voltage.Jeff, OP mentions 440 V motor, so the source is 440 V.
Using a 500 hp motor rated at 440 V with a 6-pulse drive rated at 600 A can lead to compatibility issues. The drive may not be able to provide the necessary voltage and current required by the motor, potentially causing inefficient operation or even damage. It's crucial to ensure that the drive and motor ratings match to avoid these problems.What happens if you try to use a 500 hp motor, rated at 440 V , with a 6-pulse drive, rated at 600 A?