rockman7892
Electrical
- Apr 7, 2008
- 1,156
We are considering using two 5000kVA 13.8 V-480V transformers for a M-T-M 480V unit substation to feed 6000A 480V Switchgear. The normal load calculations on each transformer with the tie breaker open is about 3000kVA and 2500kVA which would be well within the transformers rating. During a situation where one transformer out of service and the tie breaker closed the calculated load on each transformer would be a little more than 5000kVA.
I've never seen a transformer this large be used for this type of application so I was curious to hear the thoughts of others for using a 5000kVA transformer on a LV Substation?
The two downsides that come to mind are the large amount of available secondary fault current and high Arc Flash Hazard, although the Arc Flash hazard would be high on the secondary for most any transformer used in this application.
I supposed these transformers could be sized to 3750kVA or maybe even lower since this would be adequate for normal conditions and utilized the transformers increased forced air cooling during a tie situation. Is this utilization of the forced air cooling under a tie condition a standard practice?
I've never seen a transformer this large be used for this type of application so I was curious to hear the thoughts of others for using a 5000kVA transformer on a LV Substation?
The two downsides that come to mind are the large amount of available secondary fault current and high Arc Flash Hazard, although the Arc Flash hazard would be high on the secondary for most any transformer used in this application.
I supposed these transformers could be sized to 3750kVA or maybe even lower since this would be adequate for normal conditions and utilized the transformers increased forced air cooling during a tie situation. Is this utilization of the forced air cooling under a tie condition a standard practice?