electricpete
Electrical
- May 4, 2001
- 16,774
We have 6 500HP horizontal sleeve bearing motors which were purchased with winding RTD’s and bearing thermocouples installed in the motor.
These temperature sensors were not connected to any plant computer and are only monitored manually on an infrequent basis. The motors have been in operation for 14 years with no known problems. Bearing vibration is monitored approximately every 3 months and we try to take oil samples annually.
Standard practice in new construction would be to monitor and alarm these temperatures by computer.
Now I am faced with a question. Should we go through the trouble of hooking these temperature sensors to our computer. I would like to see it done but the cost to run cables will be high and I would have to justify the need to spend that money.
** Are there any standards that cover the subject of whether sleeve bearing and winding temperatures should be alarmed for this size motor?
What is the likelihood of a rapidly developing fault that will wipe out the machine before we have a chance to detect and act. (I can think of an easy one… loss of oil due to leak… we have no indication until the machine trips). Any comments on other possible failure scenario’s.
Any other comments about the pro’s and con’s?
Thanks.
These temperature sensors were not connected to any plant computer and are only monitored manually on an infrequent basis. The motors have been in operation for 14 years with no known problems. Bearing vibration is monitored approximately every 3 months and we try to take oil samples annually.
Standard practice in new construction would be to monitor and alarm these temperatures by computer.
Now I am faced with a question. Should we go through the trouble of hooking these temperature sensors to our computer. I would like to see it done but the cost to run cables will be high and I would have to justify the need to spend that money.
** Are there any standards that cover the subject of whether sleeve bearing and winding temperatures should be alarmed for this size motor?
What is the likelihood of a rapidly developing fault that will wipe out the machine before we have a chance to detect and act. (I can think of an easy one… loss of oil due to leak… we have no indication until the machine trips). Any comments on other possible failure scenario’s.
Any other comments about the pro’s and con’s?
Thanks.