575V 60 Hz 3-ph 1HP motor- any use for it?

Status
Not open for further replies.

TheRocketScientist

Mechanical
Feb 19, 2009
20
0
0
US
I have a nice new 3-phase motor. However, because it's 3-phase, it has limited use around the house. Also, it's 575V [and appears to not be re-wireable for other voltages]. Rated 1HP.

Any use for this thing? Dummy motor for 1ph => 3ph converter?

I guess it can be run on 480V, but torque will be somewhat lower as a result?

Tips appreciated.
 
Replies continue below

Recommended for you

At 480V, you will only get around 62& torque out of it, which means if you put much of a load on it, you are risking early demise.

Put it on E-bay for Canada, someone up there will buy it.