dumitruN
Electrical
- Apr 23, 2006
- 7
I have a 4" pvc underground conduit incased in concrete.
Can I put in it three triplex 5kv cables (3c)
one #1, one #2 and a #6) going from the switchgear to three diferent transformeers? I don't have a IEEE 835 standard?
The NEC tables are limited to 2000V. The power company people are telling me that they use to install one cable per conduit, but I have just one 4" conduit.
Thank you.
Can I put in it three triplex 5kv cables (3c)
The NEC tables are limited to 2000V. The power company people are telling me that they use to install one cable per conduit, but I have just one 4" conduit.
Thank you.