petroelecric
Electrical
- Jan 24, 2012
- 2
Dear Friends,
I am new to this forum and finds it very informative and all the members very much helpful in solving the issues.
We have problem with a 6.6 KV Motor and the case history is written below. Can anyone give any clue to this issue of overheating?
Rating : 355kw, 6600V, 35.5A, 50Hz
RPM : 2987.Make Toshiba F&G
Degree of Protection : IP56
DOR : CW viewed from DE side
DE Bearing : 6318C3
NDE Bearing : 6318MC3VL024.1
Insulation Class : F
Driven Equipment : Centrifugal Pump (Service : Lean Solvent)
1ST Failure : During Commissioning observed Rotor fan bolt looseness and touching stator winding which resulted into slight damage to the winding.
Action : Winding damage repaired by wrapping.
Motor has averaged running period of almost 6 months without any abnormality till 2nd failure on 18th Aug 2011.
2nd Failure : On 18th Aug 2011, Motor DE side Bearing seized and smoke was observed.
Action : Motor shaft, Bearing Housing repaired. Bearings replaced.
3rd Failure : On 25th Sep 2011, After repair of 2nd Failure immediately during load trial Motor DE side Bearing seized and smoke was observed.
Action : Motor shaft repaired and Bearings were replaced with the procedure guided by Vendor.
Following the Repair after 3rd Failure, Motor No-Load Trial conducted at site on 12.01.2012. Following were the observations.
Motor winding temperature was found to be increasing abnormally. After almost 4 hours of running, winding temperature reached 130C and was still on increasing trend. Hence we decided to stop the motor.
Motor Bearing Vibration and Temperature were found normal during the run.
Motor No-Load Amps were also found normal.
Motor IR value and Winding R is healthy.
Motor core-loss test was done and found OK.
Motor solo run at reduced voltage was done and observed no temperature rise. Motor was running normal.
Experts, kindly give your feedback.
Regards,
george
I am new to this forum and finds it very informative and all the members very much helpful in solving the issues.
We have problem with a 6.6 KV Motor and the case history is written below. Can anyone give any clue to this issue of overheating?
Rating : 355kw, 6600V, 35.5A, 50Hz
RPM : 2987.Make Toshiba F&G
Degree of Protection : IP56
DOR : CW viewed from DE side
DE Bearing : 6318C3
NDE Bearing : 6318MC3VL024.1
Insulation Class : F
Driven Equipment : Centrifugal Pump (Service : Lean Solvent)
1ST Failure : During Commissioning observed Rotor fan bolt looseness and touching stator winding which resulted into slight damage to the winding.
Action : Winding damage repaired by wrapping.
Motor has averaged running period of almost 6 months without any abnormality till 2nd failure on 18th Aug 2011.
2nd Failure : On 18th Aug 2011, Motor DE side Bearing seized and smoke was observed.
Action : Motor shaft, Bearing Housing repaired. Bearings replaced.
3rd Failure : On 25th Sep 2011, After repair of 2nd Failure immediately during load trial Motor DE side Bearing seized and smoke was observed.
Action : Motor shaft repaired and Bearings were replaced with the procedure guided by Vendor.
Following the Repair after 3rd Failure, Motor No-Load Trial conducted at site on 12.01.2012. Following were the observations.
Motor winding temperature was found to be increasing abnormally. After almost 4 hours of running, winding temperature reached 130C and was still on increasing trend. Hence we decided to stop the motor.
Motor Bearing Vibration and Temperature were found normal during the run.
Motor No-Load Amps were also found normal.
Motor IR value and Winding R is healthy.
Motor core-loss test was done and found OK.
Motor solo run at reduced voltage was done and observed no temperature rise. Motor was running normal.
Experts, kindly give your feedback.
Regards,
george