Arba
Electrical
- Jan 21, 2010
- 5
I’m having a case where from my power monitoring on the main 4000 Amp, 600 V bus fed from a 4MVA, 44KV – 600 V Transformer I see a lot of harmonic generation from a 300 KVA compressor, and different electric welding machines of the plant. The average voltage during one week monitoring is just 1.59% lower then 346.41 V (600 V) Ref Voltage. The average load of the transformer is just above 25% of its nominal load. The average amps draining on ground wirer towards the transformer is 50 A, wile the average amp on main neuter is jus 6 A. Right now the max voltage is 616.61 V and the minimum one is 550 V. Without involving any filter, would I be able to deal with the voltage drop complain from costumer only by increasing the voltage by 2.5% and bring the max voltage to 632 V or this would stimulate more voltage spikes on the plant?