I have a 3 phase 3 wire 600V service to a commercial building. The tenant experiences flickering or dimming of the lights, and her UPS's are constantly switching between battery and normal. This is consistent with a sag. Measuring on the line side of the main switch, we get:
A-B, A-C, B-C all approx 600V, which is expected.
However, referencing ground we get A-G at 540V, B-G at 587V and C-G at 59V. I would have expected 347V from phase to ground. Furthermore, why is C-phase inconsistent with the others? Our initial thoughts were that perhaps a fuse was blown and that phase was backfeeding. We have not confirmed that a fuse has not blown (with the exception of the fact that 3 phase motors are all still working, but that could be attributed to single-phasing), but is there something else I should be looking for? I have a funny feeling that something is wrong with the ground at the main board. Other than that, I think that I may have to start looking to the street and the local utility for problems with their transformers.
A-B, A-C, B-C all approx 600V, which is expected.
However, referencing ground we get A-G at 540V, B-G at 587V and C-G at 59V. I would have expected 347V from phase to ground. Furthermore, why is C-phase inconsistent with the others? Our initial thoughts were that perhaps a fuse was blown and that phase was backfeeding. We have not confirmed that a fuse has not blown (with the exception of the fact that 3 phase motors are all still working, but that could be attributed to single-phasing), but is there something else I should be looking for? I have a funny feeling that something is wrong with the ground at the main board. Other than that, I think that I may have to start looking to the street and the local utility for problems with their transformers.