690v 3 phase application lead wire rating

Status
Not open for further replies.

BigMotorGuy

Electrical
Jul 27, 2009
56
0
0
US
Stupid question, but I have an application going into a 690v 3 phase system, so since the actual voltage to ground on any of the 3 legs is 690/sqrt3 = 398.4v using 600v rate wire is ok right?
 
Replies continue below

Recommended for you

You have over 600 Volts phase to phase. Use 1000 volt rated wire.
My code requires wire to be rated for the highest voltage present, NOT the highest voltage to ground.
Bill
--------------------
"Why not the best?"
Jimmy Carter
 
TBE, in regard to the peak voltage versus RMS, wiring ratings are RMS values, so I don;t believe that is an issue.

Waross, if each individual wire is rate at 600v between the inner conductor and (in this case) the out SST armor (i.e. ground), then having 2 cables next to each other (i.e. the 690v) has 2 layers of said insulation. The problem comes in that this is specialty wire that is not available in 1kV rated. Is my thinking way off here?
 