What is your next lower voltage level? This seems to be an awfully high voltage for feeding individual buildings. If you buildings are fed with 2,400Y4,160 volt to 19,920Y34,500 circuits, you might want to think about eliminating the 69 KV level. Ohio Edison has replaced some 69 KV primary 7,200Y12,470 volt secondary distribution substations with 138 KV primary substations.
Is your 69 KV ring bus confined to just this campus or does it serve other customers?
With the advances in SF6 switchgear, insulators, and solid dielectric cables, you can often run a 138 KV or 161 KV circuit for less money than 69 KV. About the only real difference is spacing between wires and open ( air insulated ) busbars.
You also need to consider that with a 1,000 KCM conductor you will have a hard time getting more than about 3/4 of the wire strands to conduct unless the connection is welded. You can get aluminum lugs that are intended to be tungsten inert gas welded to the end of ACSR transmission conductor. In fact, I would not consider any connection method for this wire size other than welding. Since aluminum is easier to weld I would shy away from copper. If you want to play around you could splice aluminum conductor using electroslag welding but that would really only work on transmission conductor.
Copper is much harder to weld than aluminum which is one reason why I do not like knee jerk prejudice against aluminum wire. About the only welding method that works on copper is exothermic welding which would not work for an underground cable. This is because it takes about 6 times as much heat to weld copper than aluminum. In fact, it takes less heat to weld steel than to weld copper.
A lot of "aluminum" wiring failures were later determined to be caused by something else and it turned out that there were other factors that caused a lot of copper wiring failures. Among them were cheap steel terminals in 69 cent outlets, not cleaning off the aluminum oxide, and so forth. Also, Federal Pacific, Wadsworth, and Zinsco circuit breaker would develop arthritis and allow a circuit to carry 150% to 300% of its rating. Reynolds also made a rather soft aluminum alloy that aggravated things and Alcan has been able to prove that their alloy is by far superior.
Also, Dr. Jesse Aronstein (
) ran some test that showed that a wire brush is 100% INEFFECTIVE at removing aluminum oxide. The most effective agent is #220 silicon carbide abrasive paper. I also have directions on how to get ALL the wire strands of copper or aluminum wire to conduct over at