rockman7892
Electrical
- Apr 7, 2008
- 1,159
I'm working with a customer to replace an existing 69kV GIS lineup that was recently identified as being ovedutied for SC due to the significant amount of generator fault contribution connected to the lineup. The fault contribution to this lineup as shown comes from utility fault source (138kV Substation), generator contribution, and 15kV & 4.16kV motor contribution downstream. This existing lineup feeds several downstream 15kV & 4.16kV lineups which are M-T-M lineups operated with tie breaker normally CLOSED.
The customer has suggested building a new 69kV GIS lineup to move the majority of the generators over the new lineup to remove their fault contribution to the existing GIS lineup (See attached one-line). They did not think they had the flexibility to replace the existing lineup with adequately rated gear without significant downtime so wanted to explore a new 69kV GIS lineup as shown with moving (6) of the generator units over to the new GIS lineup. A new future utility source from the 138kV substation will also be added to this new lineup.
With removing (6) generators from the existing lineup and leaving (3) generators as well as the existing utility source the existing lineup is within its fault duty rating. The majority of the downstream 15kV/4.16kV loads will continue to be fed from this lineup. With this arrangement however there would not be able to be a tie breaker between the (2) 69kV lineups due to the fault contribution from the generators on new lineup feeding back to the existing lineup. All downstream 15kV lineups are ran with Tie Breaker NC.
Does this seem like a practical approach here? Any considerations for the new lineup and redundancy with lack of tie between two 69kV lineups?