As a QC performing observations of A325TC bolts does code require the ends to be snapped off?
 
Replies continue below

Recommended for you

Tension Control Bolts assemblies come with their own built in tension control device (spline) to ensure dependable and repeatable tension levels are achieved with each installation. They are installed with a specialized electric shear wrench that has an outer socket that turns the nut counterclockwise, while grabbing the spline with the inner socket turning it clockwise. When the proper tension level has been achieved the spline snaps off giving you a visual indication of proper installation. Specification: A325/F1852 & A490/F2280
 
Only if pretension is required. TC bolts are acceptable in snug tight applications, and the splines do not need to be snapped in these cases.
 
sbisteel has got it. As a QC personnel, you are going to be mainly concerned with the lubrication on the bolt assembly being intact otherwise you may see premature shearing of the spline. As a side note, didn't ASTM A325 get replaced with ASTM F3125 recently?
 

Yes, a while back, and Grade A325 bolts are part of it.


Dik
 
You're listed as a Military Engineer - pay close attention to your specs and governing code. The structural UFC (Unified Facilities Criteria, the building code for NAVFAC and US Naval bases) require TC bolts or DTI washers on ALL bolted steel connections. I can't imagine they'd require the more expensive hardware to be used everywhere and then not require it to be used for its intended purpose.

I'm not here to argue for this requirement - I've never been able to figure out a good reason for it and have come up with and attempted to argue a few reasons not to do it, all to no avail.
 
Same question as phamENG, if pretension was not required, as a QC, I would ask why the bolt was used for.
 
Using TC bolts everywhere has a few advantages. Mainly, it reduces site labor - the TC gun holds the bolt and the nut which means you only need 1 ironworker to install the bolt. Since the TC gun holds the nut and the bolt, there is no external force required to hold the TC gun from rotating, which reduces the effort required by the ironworker. The 2nd big advantage - you can install the bolt from one side of the joint only...you just need enough room to slip the bolt through the backside of the connection and then you can tighten from a single side.

TC Bolt Installation
Standard High Strength Bolt Installation (notice the guy on the opposite side of the joint)
 
Tell you the truth, I've never see two guys work on twisting a bolt, except where safety rule called for, or there is something large and heavy that require more than a few bolts.
 