jrw501
Structural
- Mar 2, 2009
- 85
I’m looking at designing anchor rods at a fixed pier of a 3 span continuous bridge (E-F-E-E) to meet AASHTO 3.10.9.2 requirements of the horizontal design connection force of 25% of the vertical reaction due to tributary permanent load and live load assumed to exist during an earthquake.
Because the fixed pier connection has to transmit 25% of the vertical reactions for the whole bridge, it’s seemingly very difficult to meet some of the ACI-related anchor provisions (particularly regarding breakout shear unless the pier is made to be super wide or stirrups/hairpins are provided around the anchor group and if we’re to assume only a few anchors in the group take the full load). The anchors themselves are no problem to design for the load.
Are there some typical assumptions people make to get around these in a pier cap/bent cap? Maybe counting on cap stirrups to restrain failure surfaces in an extreme event for example? Using friction to reduce applied horizontal forces on the anchors? I've looked at two other projects (one with virtually the same span arrangement and pier width, but a narrower bridge with few girders) that were designed for the same DOT, but it doesn't look like any special considerations needed to be made at the fixed bearings. I'm not particularly concerned, but I'd certainly still like to make it work on paper.
Thanks!
Because the fixed pier connection has to transmit 25% of the vertical reactions for the whole bridge, it’s seemingly very difficult to meet some of the ACI-related anchor provisions (particularly regarding breakout shear unless the pier is made to be super wide or stirrups/hairpins are provided around the anchor group and if we’re to assume only a few anchors in the group take the full load). The anchors themselves are no problem to design for the load.
Are there some typical assumptions people make to get around these in a pier cap/bent cap? Maybe counting on cap stirrups to restrain failure surfaces in an extreme event for example? Using friction to reduce applied horizontal forces on the anchors? I've looked at two other projects (one with virtually the same span arrangement and pier width, but a narrower bridge with few girders) that were designed for the same DOT, but it doesn't look like any special considerations needed to be made at the fixed bearings. I'm not particularly concerned, but I'd certainly still like to make it work on paper.
Thanks!