Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

AASHTO LRFD Code on Concrete Flexure Member Section Proportion Limit 1

Status
Not open for further replies.

Stewie_

Civil/Environmental
Aug 18, 2010
16
Hi, Dear All,

Is there an RC flexural member section proportion limit in the aashto lrfd code? Liks depth/width ratio limit?
If not, is there something like this in the ACI or IBC codes?
Please help, Yo~

Best Regards,
Stewie
 
Replies continue below

Recommended for you

In ACI there definitely are some limits scattered throughout that infer a required width to span/depth ratio is required.

Refer to clause 9.2.3.1 for general stability requirement based on member width in relation to points of restraint and refer to clauses 18.6.2.1 for some limits applicable to beams in special moment frames. All references based on ACI318-14.
 
Hi, Dear @Agent666,

Thank you so much for the help.

:p
Stewie
 