Toasted, it may well be that no PLC is needed. As CJCPE has suggested earlier, if you choose the Hand/Auto Macro in Parameter 9902, you get the ability to have two different configurations with the same drive---the selection being made with one switch closure on Digital Input 3 Terminal 15.
When that switch is open, the drive looks to Analog Input 1 Terminal 2 for its speed command, and when that switch is closed, it looks to Analog Input 2 for its speed command.
You will notice that the Start/Stop and Forward/Reverse is also on different terminals depending on whether that switch on DI3 is open or closed. If you want them to both be on the same terminals so only the speed command moves, let me know and I'll give you the Parameters to change.
On the other hand, if all you want is up to seven fixed speeds, then use the ABB Standard (default) Macro and we will help you configure the inputs for seven fixed speeds. The default is three fixed speeds but it is easy to change that to seven.