ABB REG 316*4 Communication

Status
Not open for further replies.

Shark96

Electrical
Feb 24, 2015
42
Hello. I have to translate stator earth fault settings from REG 316 to the newer model REG 316*4. I do not have the optical cable for communicating with PC. There is also a serial port at the back of the new relay. However, the relay is not communicating using the serial port (I used a 9pin serial to usb cable). Can anyone guide me regarding this?
 
Replies continue below

Recommended for you

Try a null modem adaptor. They make small DB9 adaptors that fir right on the serial cable. Else you can modify an existing serial cable to swap the TX & RX pins.
 
I don't think you can use the rear serial port to change the settings. Only the front optical port.
You need the special serial to optical cable:


Serial interfaces
• Frontplate interface for local connection of a personal computer
• Back plane interface for remote communication with a station control system: LON, IEC60870-5-103, MVB (part of IEC 61375), SPA
• Back plane interface for process bus: MVB (part of IEC 61375).
 