In this thread you mentioned above ground test for B31.8 piping is not to see for leaks, it is to verify strength.
I have a follow up question on this,
IF a test is done under B31.4 above ground for a manifold with many diameters pipe, during this test the inspector somehow did a continous bleed for 3 hours of the test inorder to nullify the pressure variations due to temperature. I would like to ask if this test is acceptable as per code as an above ground 4 hour test?
What if he had collected the volume of water water he bled?
WHat if the volume was not measured?
Always be a Student
In this thread you mentioned above ground test for B31.8 piping is not to see for leaks, it is to verify strength.
I have a follow up question on this,
IF a test is done under B31.4 above ground for a manifold with many diameters pipe, during this test the inspector somehow did a continous bleed for 3 hours of the test inorder to nullify the pressure variations due to temperature. I would like to ask if this test is acceptable as per code as an above ground 4 hour test?