AC Hi pot Test

Status
Not open for further replies.

zaza123

Electrical
Dec 3, 2008
103
we are doing AC hiPot test for Medium voltsge cables,the volateg level is 4.16 kV & 13.8 KV .for 4.16 KV , the isulation withstand level for 4.16 Kv is 6/10 Kv ,so we can inject 3 times Uo (ie 18kv) FOR 1 hOUR. I am under the impression that this is as per VDE standard , can somebody confirm this
 
Replies continue below

Recommended for you

You need to follow manufacturer's recommendations. IEEE no longer recommends hi-pot testing for MV cables, IIRC.

Search this forum. This has been discussed previously.
 
I remember IEEE has reduced discussion of dc hi-pot of cables (if memory serves me right, it's still listed in but not necessarily recommended)

I didn't realize the same applied to ac hi-pot. Does it?

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
AC hipot is still OK, but a 60Hz an AC hipot needs a ton of power to charge a MV cable of any signifigant lengh, thats why VLF is used instead of power frequency for AC cable hipotting.

I will need to double check your testing specs Monday but sounds right to me. (Not sure an hour is necessary, you dont mean 1 hour per phase do you?)
 
My bad - I missed the ac reference.
 
We insert 0.1hz frequency, all the Phases are joined together & for 4.16 KV cable (insulation level 6/10 KV)we give 3Uo ie 18KV for 1 hour, the leakage current in one sample we got 3.1mA.This particular method was advised by the Testing company.so the voltage which we are giving is given to three phases simultaneoulsy.

 
i forgot to add the reference CENELEC HD 620 S1 part 5 Sction C (indent with the German Norm VDE 0276-620)
 
So you are using VLF, should be good. Cant help you with the spec (In the USA) we follow ANSI/NETA, IEC, and IEEE specs, dont have the VDE. Even so, an hour sounds like a long time to test 1 phase.
 
While doing this test we are connecting all the three phases of the cable ie L1, L2 & L3 together ,is it right or it should be done seperately for each phase.
 
Seperate, you will want to compare the results between the 3 phases, unless you are a testing company that does this for a living and have a large database of test results comparing phases is all you really have to go on for condition assesment.
 