Thedroid
Electrical
- May 18, 2008
- 196
After combing through the manual I still can't determing how this unit differentiates a Ground Fault from a Long Time, Short Time, or Instantaneous Fault. They are installed on a 480 Wye three wire secondary.
After playing around with the tripping time calculator on the Utility Relay Company website, It seems like there is no difference. Just different names for different curves.
If this is the case, it seems that the GF setting would have to be set higher than all others, or the unit would always trip on GF.
After playing around with the tripping time calculator on the Utility Relay Company website, It seems like there is no difference. Just different names for different curves.
If this is the case, it seems that the GF setting would have to be set higher than all others, or the unit would always trip on GF.