Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Acceptable Test Values for new 2KV cable.

Status
Not open for further replies.

EPSarizona

Electrical
Feb 15, 2003
1
US
When testing 2kv Cable (unshielded) that will be used in a 900vdc system, what are the acceptable results for a megger test at 2kvdc? The design engineer calls for a PI as well. One run has a PI of less than 1 but has a ten minute read of 600 Megohms.
 
Replies continue below

Recommended for you

EP,

Our company standards would be a 1kV megger test with a minimum IR of 100 Mohms. It is not a normal test for a PI on a cable and I am not sure why this has been specified. A PI minimum of 2 is for equipment.

Cheers, Coingy
 
Status
Not open for further replies.
Back
Top