Guys,
We have in our plant a 230 /13,8 kV 31 MVA transformer that had the following DGA result (in ppm):
H2: 228
O2:15400
N2:74000
CH4:41
CO: 297
CO2:1570
C2H4:64
C2H6:9
C2H2:179
Total:818
After this result, we did the ultrasonic test to locate some partial discharge inside the equipment. The result indicated that might have been some problens around the OLTC. So, we decided to call the OLTC manufacturer to do a full inspection at the OLTC.
They found some loose conection between the switch and tap windings. We repaired these connections and we treated the insulating oil to remove the gas dissolved. Then we put the tranformer to operate again. In the latest DGA, we notice that acetylene level is rising again.
My question is: Is it possible that some acetylene was trapped in the transformer paper and insulation and now they are being released or there are another problem inside the transformer?
I am attaching the loose concections picture.
Thanks
We have in our plant a 230 /13,8 kV 31 MVA transformer that had the following DGA result (in ppm):
H2: 228
O2:15400
N2:74000
CH4:41
CO: 297
CO2:1570
C2H4:64
C2H6:9
C2H2:179
Total:818
After this result, we did the ultrasonic test to locate some partial discharge inside the equipment. The result indicated that might have been some problens around the OLTC. So, we decided to call the OLTC manufacturer to do a full inspection at the OLTC.
They found some loose conection between the switch and tap windings. We repaired these connections and we treated the insulating oil to remove the gas dissolved. Then we put the tranformer to operate again. In the latest DGA, we notice that acetylene level is rising again.
My question is: Is it possible that some acetylene was trapped in the transformer paper and insulation and now they are being released or there are another problem inside the transformer?
I am attaching the loose concections picture.
Thanks