With respect to typical cast-in headed anchor rods I note that Hiti Profis and Simpson Anchor Designer both limit you to a minimum spacing of 6 x diameter; it is my understanding this is the requirement for post-installed only and one can go down to a minimum 4xD for cast-in when evaluating per ACI 318-14 is this note correct?
Also I note Profis will not let you go more than 25 inch embedment; it was my understanding this was a limit in ACI 318-08 but was removed as of ACI 318-11 and beyond...is ACI 318-14 breakout equations not applicable to over 25 in embedment?