We typically have very high loads and per our company standards, this ends up requiring longer than typical embedment depths for anchor bolts/rods.
I'm using 318-02 for a design right now, and D.5.2.2 gives the equations for breakout strength, but only provides equations for up to 25" embedment, which according to the commentary was the limit in their testing.
Can I assume (always a risk) that the equation is acceptable for embedments greater than this? ie 30" or even more?