justhumm
- May 2, 2003
- 112
I have a question regarding concrete pullout & side-face blowout requirements for a highly loaded anchor bolt(s) in tension. This bolt will be supporting a column base plate that sits on a drilled shaft, which will have a (yet to be designed) rebar cage of some sort.
Taken from the "8 Nov 14 22:26" response on this thread:
[URL unfurl="true"]http://www.eng-tips.com/viewthread.cfm?qid=374061[/url]
And there's a paragraph in ACI-318 (08, in front of me) D.5.2.9 that states:
Is there an ACI/CRSI document or paragraph that makes a similar statement with regard to Pullout (D.5.3) and Side-Face Blowout (D.5.4)?
i.e.: Is there definitive statement somewhere that says if you provide a sufficient rebar cage, with a long enough anchor rod, you can ignore the pullout & blowout requirements of Appendix D?
Thanks for the feedback!
As far as development goes, it is perfectly acceptable to lap an anchor with a rebar cage. The same rules would apply as for non-contact lap splices. Presumably the anchor rods would be inside the confined core of the foundation, so most of the limit states from App D are restrained by the surrounding reinforcement, i.e., "supplemental reinforcement." Appendix D is typically applied to reduce the embedment depth to less than a typical Ld. Also, many anchors are higher capacity than a similarly-sized rebar, making a strict lap a bit difficult.
Where anchor reinforcement is developed in accordance with Chapter 12 on both sides of the breakout surface, the design strength of the anchor reinforcement shall be permitted to be used instead of the concrete breakout strength in determining φNn...