I'm in the process of designing a wedge anchor connection per appendix D of ACI 318-08. I'm trying to figure out when to assume cracked vs uncracked concrete.
When anchoring to a compression zone, one would assumed uncracked concrete and cracked for tension zone.
What happens when you anchor to a compression zone in a seismic area? Do you assume cracked? or can you still assume uncracked?
When anchoring to a compression zone, one would assumed uncracked concrete and cracked for tension zone.
What happens when you anchor to a compression zone in a seismic area? Do you assume cracked? or can you still assume uncracked?