cpb213
Structural
- Apr 22, 2019
- 7
I am designing a deep shaft (100' deep) that has multiple landings for stairs at different elevations and the contractor is questioning our design stating that it is too conservative.
The shaft resists soil on one face only so the reinforcement was controlled by out-of-plane bending. We designed the reinforcement in accordance with ACI 318-14 Chapter 11.1.4 which determines the required reinforcement due to flexure. We provided a minimum tensile flexural reinforcement ratio equal to 0.0018 which was based on the minimum flexural reinforcement ratio for a structural slab (ACI 318-14 Chapter 7.6).
The contractor thinks that we don't need to follow the Chapter 7 minimum reinforcement requirements for slab and just need to provided the required reinforcement from the flexural forces and follow the minimum requirements for a wall (ACI 318-14 Table 11.6.1). They also believe that we can use the provisions of ACI 9.6.1.3 which allows you to ignore minimum reinf. requirements if you provide 33% more steel than required.
To summarize my question:
For a wall in which the reinf. is controlled by out-of-plane flexure, do I need to meet the min. tensile reinforcement requirements for structural slabs? Does ACI state that somewhere?
The shaft resists soil on one face only so the reinforcement was controlled by out-of-plane bending. We designed the reinforcement in accordance with ACI 318-14 Chapter 11.1.4 which determines the required reinforcement due to flexure. We provided a minimum tensile flexural reinforcement ratio equal to 0.0018 which was based on the minimum flexural reinforcement ratio for a structural slab (ACI 318-14 Chapter 7.6).
The contractor thinks that we don't need to follow the Chapter 7 minimum reinforcement requirements for slab and just need to provided the required reinforcement from the flexural forces and follow the minimum requirements for a wall (ACI 318-14 Table 11.6.1). They also believe that we can use the provisions of ACI 9.6.1.3 which allows you to ignore minimum reinf. requirements if you provide 33% more steel than required.
To summarize my question:
For a wall in which the reinf. is controlled by out-of-plane flexure, do I need to meet the min. tensile reinforcement requirements for structural slabs? Does ACI state that somewhere?