active- reactive energy electromechanical meters

Status
Not open for further replies.

ftova

Electrical
Jan 27, 2017
2
hi everybody

what`s difference in construction between active and reactive energy electromechanical meter?
may it turn active energy electromechanical meter into reactive energy electromechanical meter or viceversa?

url`s, pdf`s or comments are wellcomed

thanks in advance

Fredrick
 
Replies continue below

Recommended for you

Same meter.
At one time Kilo-Watt-Hour revenue meters were used to meter both real energy and reactive energy.
As I remember, an induction coil was connected in series with each potential coil of a standard KWHr meter.
This caused the voltage to lag 90 degrees in the potential coils.
As a result the meter reacted to and metered reactive energy.
It's been a long time since I installed those meters and he details are a little hazy, but I remember the phase shifting inductor that was an available accessory for metering reactive power.
The monthly average power factor was determined from the monthly Kilo-Watt-Hours and the monthly Kilo-VAR-Hours.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 