Adding Studs to Existing Composite Beam 3
PEinVA
321
I am adding a large stair to a steel composite building. I am having difficulty getting the existing beams to work. The girder that the beams frame into was overly designed while the beams were designed just below failure at 100 PSF LL. With the additional load even adding a WT section under the beam does not keep the stresses below both 0.66Fy and 0.9Fy checks. Has anyone added studs to an existing beam? I cannot find any information about this and was wondering if it had been done before. Thanks.
RC
All that is necessary for the triumph of evil is that good men do nothing.
Edmund Burke
How would you add studs to an existing concrete slab/composite steel beam? Isn't the slab already poured, the studs already encased with concrete?
I think I've heard about this with coring out the concrete deck, welding the studs, and grouting. But I could have dreamed it.
Hg
Eng-Tips policies: faq731-376
The thought is, if you core to the top of the flange, and weld new studs on, and repour non-shrink grout, it would act as one. Thus adding composite action to the existing beam.
RC
Edmund Burke
It depends what % composite you are at. If you are already at 100% composite, then I can't imagine that adding studs will help.
If you aren't a terrible amount of load you should be able to get a WT to work. I had some existing (non-composite) WF beams where the space was being changed from 40 psf LL to 100 psf LL and I needed a relatively large WT, but I was able to get it to work. What kind of additional loads are you looking at? Can you get creative with adding a WT with a channel on the bottom flange of the WT?
The problem is I'm at 40% composite existing. When I add the new load, I drop to 25% composite. The more steel I add, the steel starts to control and requires more studs, which then causes me to drop below the minimum of 25%. This is why I'm asking if adding more studs is conceivable. I can only add 5.2 in^2 of steel before I drop below 25% and I am at 44ksi<0.9*50 ksi and at 34 < 33 ksi. (Elastic check). This case is for the more lightly loaded beam.
RC
Edmund Burke
I went thru my collection of papers on strengthening existing steel members. Many of them address adding studs to existing non-composite beams, but none of them deal with adding studs to existing composite beams.
The most appropriate paper for your situation might be article in Second Quarter 1996 AISC Engineering Journal, "Strengthening of Existing Composite Beams Using LRFD Procedures". That says "This paper deals with the addition of either a flat steel plate or a WT section to the bottom of the beam to moderately increase its load carrying capacity. For a major increase in capacity,the method described in this paper could easily be extended to other reinforcing shapes".
If you have a partial composite beam, and apparently you do, there is absolutely no problem coring and adding steel studs to increase the percent composite action. We have done exactly this on several occasions.
Just core the holes large enough for the stud welder, and at least four times the diameter of the head of the stud for grouting purposes, and be certain that you use a non-shrink grout (at least equal in compressive strength to the concrete slab) to fill the hole. Stud size should be as normally designed for new composite beams.
Also, if you have excessive deflection under the proposed load (or even under the existing loads if the beam was mistakenly underdesigned), jack up the beam slightly before adding the additional studs to transfer the dead load to the composite section.
Strengthening by adding cover plates to the undersdie of the beam is also a relatively simple procedure, which we have done in numerous existing buildings. For economy in field welding, try to use a plate wider than the flange so that the welding is performed in a comfortable position, instead of overhead. Also, design the cover plate and the welding to suit the loading conditions, do not be overly conservative by specifying a continuous weld, and cut-off the ends where approriate. A full length cover plate is never required.
Note that jacking of the girder before welding the cover plate will also transfer the dead loads to the composite section. (Place the plate in position, then jack against the plate, clamping it against the underside of the beam.)
OK its Saturday - I'm a bit slow today - but how does adding load to a composite beam change its percent composite value? That is a static value based on geometric properties is it not?
I would second epr's comments. Been done before. But I would first try to add steel to the bottom of the beam as its probably much more cost effective.
JAE - adding load doesn't but adding a WT does - Percent composite is calculated by the force that can be transferred into the concrete by studs divided by AsFy of the steel section - increasing AsFy by adding cover plates or WTs therefore reduces the composite percentage.
That (and that fact that the ductility required of the studs to perform efficiently at 25% composite is extremely high) is the reason why I rarely go much less than 40-50% composite. $15 worth of shear studs saves a lot of headaches later.
WillisV-
Percent composite being controlled by AsFy is only true if the PNA is at or above the top of the top flange, correct? If the PNA is in the steel section then the percent composite is related to Ac(f'c)?
Dont know if I have a complete understanding of the problem but why not add non composite beams between the existing composite beam at the new stair location to cut down on the tributary width of the would be overstressed composite beam. You stated earlier that the main girder beam was overdesigned so the addtion of these new beams should be no problem.
WillisV,
That is exactly my problem. When adding steel, it increases my required studs for full composite and decreases my percent composite.
StructuralEIT,
In any calculation I have about composite it only shows the caluclation of 0.85f'cAc/2 and AsFy/2. It doesn't seem to correlate to any other calculations.
CowboyBill74,
The client is already upset about having to add 8' W8's between the existing W14's. We are at the 15th floor of an existing building and getting the steel in for the stairs is going to be a job in itself. I'm trying to reinforce in the simplest(also somewhat smallest) way possible.
epr,
Do you have any papers, research supporting the methods you use/describe? Can you please let me know where I could find them. Thank you.
Thanks for all the input.
RC
Edmund Burke
I have added studs to existing composite beams, by core drilling holes along the length of the beam and welding studs to the beam flange. The cores were filled with grout. This was many years ago, and was successful in upgrading floor capacity.
Thanks for the reply ironmon. Do you have any research/reports/data on this type of reinforcement. I can't seem to find anything. Anything would be greatly appreciated.
RC
Edmund Burke
You might want to contact AISC. Chris Hewitt and Bill Liddy (both w/ AISC) had article in September 2003 "Structural Engineer" titled "How to Retrofit & Rehabilitate Steel Structures". No number crunching in this article, but in the conclusion they say to contact AISC for info on the subject matter, some of which is available at or 866-ASKAISC.
RCraine-
When you get some resolution on this matter, please let me know the references you have acquired. i would be very interested in reading through them.
Can you just add enough steel underneath for the beam to behave as non-composite and ignore the studs.
or add a new beam along side to take the stair loads.
This may end up cheaper than all those cored holes and welded studs.
csd72,
It's not necessarily a matter of cost, its more of ease of construction because right now they are not sure how they are getting the steel for the stair up to the 15th floor, and it is only 11 foot in length. These are 28' spans. I think coring a few holes and adding some studs would be easier.
We'll see what the owner thinks.
StructuralEIT,
I've copied the email I received from AISC below:
"RCraine,
Although the AISC Specification and Manual to not address it, one can add additional shear studs to increase composite action. Refer to AISC FAQ 4.5.5 at We are not aware of any specific testing, so it must be approved by the EOR after considering the strength of the existing concrete and new grout (used to fill the newly added stud holes.) Additionally, one may consider adding plate reinforcement to the bottom beam flange to increase the steel beam capacity.
Sergio Zoruba, Ph.D., P.E.
Senior Engineer
American Institute of Steel Construction, Inc.
866.ASK.AISC"
RC
Edmund Burke
I'm speaking from complete ignorance here, but you might need to make sure they don't mangle the top flange in the process of coring the deck.
Hg