I have 2 cranes, running parallel; which are both loading the same steel truss.

Do I have to use the maximum loads from both cranes to design the truss or can I reduce the load somehow?
 
Replies continue below

Recommended for you

You need to find out what the minimum separation is between the two and base your calculations on that. usually it is mechanicallly limited so they can only travel to within a certain distance of each other.

I would not take accidental loads from the two simultaneously just their working loads.
 
If they can both operate at the same time, then use both loads, keeping in mind that simultaneous load conditions with the cranes at different locations need to be checked as well.
 
I would design the truss for the maximum loads, and establish a minimum separation between the cranes. Actually I did that for verification of an existing concrete crane beam. Regards,

Sebastian
 