Adjustable Pressure Relief Valve 2
Dale Carter
I'm searching for a reliable Adjustable Pressure Relief Valve to use for pneumatic piping testing. Does anyone have any advice/experience with these? Thanks in advance.
Any suitable pressure regulator can be used for supplying the desired pressure. Supply that to your pipe under test through a "quick exhaust valve". Any pressure in the pipe that exceeds the set supply pressure will be vented to atmosphere at the capacity of the quick exhaust valve.
First define what you mean.
This sounds like a device to limit pressure to a set maximum which is used as a safety device (i.e. it should never open)?
So usually this would be set at least 10% above your test pressure. Spring relief valves are very reliable and can be adjusted to different pressures.
Then you need to look at what is available from the relief valve suppliers. Most give you springs which only operate within a certain band of pressure before you need to swap springs.
Or do you mean a pressure control valve used to fill the pipe in the first place?
Pneumatic testing of piping and equipment is fraught with risks int he event of failure of any component. You need to take suitable measures to reduce risks as far as possible.
Always remember your test equipment's MAWP is the test pressure of the thing you are testing. So you may need a higher class of flange or thicker pipe than the item under test.
If testing with pressurized gas, review safety recommendations in ASME PCC 2.
and consider putting the device inside a test cell. Proof tests are supposed to prove strong enough by applying a specified over pressure. The occasional failure has considerable energy released.
In my opinion, "adjustable pressure relief valves" such as Taylor "relief valves" (Link) are not true relief valves and should not be relied upon for process/equipment safety.
They generally aren't stamped by ASME, are field adjustable meaning you never know what it's set at, and don't meet ASME B31.3 or BPVC as relief devices.
For B31.3 pneumatic leak testing, we use 1/2" NPT Swagelok R4 adjustable relief valves on our test rigs. These are set at 10%/50 psig over the test pressure. There is a human operator present at all times at the (remote) test rig who can isolate the nitrogen source and depressurize the test piece from a safe location.
We considered the adjustable relief to just be a warning that our primary regulator had failed.
We did have a permanent PRV set at 275psi which was 25psi above the highest test pressure that we ever used.