SteelPE

Structural
Mar 9, 2006
2,749
I am designing my first wood structure (a garage) and have a question about the adjustment factors. Currently I am designing a 2x6SPF No 2 stud for an exterior wall. As far as I can see, under to worst loading combination, I have the following adjustment factors.

CD = 1.6 (wind case)
Cf = 1.3
Cr = 1.15

When I multiply these together I get an increase of the allowable bending strength of 2.392x the base design values. This is quite large…. Is this correct for this condition?

Sorry about the simple question.
 
Replies continue below

Recommended for you

Yes but only for the D+L+W or D+W load combinations and only for Fb. Fc has a different CF factor (1.1)

You also have to check for the D+L condition without the Cd = 1.6 case. You'd use Cd = 1.0.

 
JAE...as usual you are da man!
 
Is there an allowance or duration increase allowed in shear capacity when designing a wood moment frame in place of a shear wall (with wind only) for either the top plates or header such as the 1.4 allowed in panels per IBC section 2306.3.2?

Example, SYP #2 as my top plates has a value of 90 psi. Can this be increased for a wind only collector and if so how much (1.4, 1.33, 1.6)?

Any opinions or thoughts are appreciated.

Thanks !
 
You should start a new thread.

 
SteelPE,

Be sure to be cognizant of the additional wall stud bending increase factor in IBC to use in lieu of Cr = 1.15. I believe it is 1.35 for a 2x6 and 1.5 for a 2x4.

I can't recall the exact provision right now, but it is in the wood section of the code. I would check that out to see if it applies to what you are doing.
 
abusementpark

In the part of the country I come from we don’t use the IBC…. We only use a state interpreted version of the IBC… and the adjustment factor only applies to studs spaced ano more than 16” o.c. My studs are spaced at 2’-0” o.c. (forgot to mention that above).

Not being used to wood design, I was just shocked that the number was so high (and it looks like you can go even higher for some cases).
 
Don't forget the allowable deflections from wind. Depending upon your wall finish these can be the controlling factor and not stresses.
 