Ed H.
Computer
- Jan 5, 2018
- 3
I am having trouble getting a pilot operated PRV to operate as I think it should. This 3 inch PRV is installed in a private, gravity-fed domestic water supply system on a mountain. There is storage tank at the top of the hill and home sites served by the system are located at various locations going down the mountain. The PRV is located half way down to keep the line pressure manageable. The upstream pressure at the PRV is approximately 120psi. I would like to reduce the downstream pressure to around 40psi.
The problem i have is when a larger downstream demand pulls water, the downstream pressure at the PRV will drop to zero and the PRV locks up in the closed position, even after the demand subsides. Then, the only way to start flow through the PRV is to adjust the red valve clockwise (closing). I would like to confirm the proper sequence/procedure for adjusting this valve. Thank you!