Advice Please: Nema Enclosure

Status
Not open for further replies.

sv879

Mechanical
Dec 7, 2018
68
I was wondering if anyone could help me with the selection of NEMA enclosure, based on the following specification.

The structure or panel shall be securely mounted in an enclosure(s) which will protect the equipment
against mechanical injury and falling drops of water striking the enclosure from the downward vertical.

NEMA2/NEMA3/something else?

Thank you!
 
Replies continue below

Recommended for you

IP Code 11 Which is a NEMA 2 Assuming it's indoors
If your outdoors go NEMA 3

There is no job too big or too difficult for the person who doesn't have to do it.

Louisiana PE
 