Aerodynamic Loading on a Cooling Tower.
floridashaughn
8
0
0
I am trying to find some information on dynamic loading (fan) on a cooling tower structure . Any help would be greatly appreciated.
Thank you,
do you mean the delta p that the fan is creating ?
or the internal airflow ?
or the external wind loading ?
Quando Omni Flunkus Moritati
Wouldn't it be the generated thrust imposed on the mounting points; action -- reaction?
TTFN
faq731-376
7ofakss
Yes, I just did not know the required variables needed. I am a young structural engineer, not aerodynamic. I have calculated thrust being F=(mass flow)(air velocity). My calculations provided a value with the units lb-ft/s^2, so I'm assuming I divide this by gravity to get lbm. The answer is coming up with a very small weight. On, another note, what exactly is the propeller efficiency coefficient. Would this be given by the manufacturer? Thank you for your help
Not my specialty, but I would have expected more like this:
You should be looking at an overturning moment, rather than a weight, I think, but, you never stated whether the fan force was acting vertically or horizontally. the equation in the cite is already in force, assuming units usage is correct. Division by g to get force is not correct.
TTFN
faq731-376
7ofakss
Sorry about that. Yes the fan is mounted vertically, pulling air from below creating a thrust (Force) reacting at the contact points. The reason, I thought, to divide this thrust by gravity would be to get my value in weight, rather than force.
Man I am tired. I guess that would give me what I need. Dividing by gravity is going to give me a mass value. So this would be right. Thank you. How would I get the propeller efficiency coefficient? Thanks
It shouldn't matter much. Your mass flow should pretty much account for efficiency. I'm a bit surprised that this is a concern at all, given that the mass of the tower must be at least an order of magnitude, if not two, larger than the lift capacity of the fan itself. I would have thought that rotational torque or nutation from the fan would be a bigger concern.
TTFN
faq731-376
7ofakss
BTW, this probably should have been posted in the Heat Transfer, HVAC, or even plain Structural forums; there probably would have been a bigger response pool
TTFN
faq731-376
7ofakss
i don't think you need propeller efficiency ... if you know the flow rate you can calc the pressure ... pressure*area = force
flow rate ... ft3/min ? ton/min ??
if ft3/min, well that is area*v (yes?) ... what you want is pressure*A = 1/2*rho*v2*A ... yes?
torque should affect the reactions as well ... some of the motor torque goes into the airflow (as swirl) but some is reacted by the fan supports.
I would think that the weight of the fan, motor and frame would far exceed the thrust created by the fan, so, I would be more inclined to calculate the support of said structure assembly.