Nandaem
Mechanical
- Mar 14, 2023
- 3
A large high rise apt community in India following IS ( mostly follow British Stds) codes is facing corrosion of 110m high of 3 X 6" CS fire mains filled with untreated bore well water in storage tanks per original flawed design. Its only 2 yrs old.The builder wants to replace corroded portion and hydro test only replaced piping at max operating pressure of 14bar. But owners association wants test at Max OP times 1.5 which is based on ANSI B 31.1.Builder is afraid of risking rupture due to lost thickness if tested at 21bar and defends their position with an IS code that allows retest at OP not 1.5OP. Also cost is an issue as builder has to pay.Appreciate comments and suggestions that could help us resolve the issue. Does any international piping code allow less than 1.5OP for aged installations?