Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

AHU approach

Status
Not open for further replies.

hvacers

Mechanical
Jan 4, 2010
26
0
0
PH


almost all of the approach of my AHUs in my building are very high eventhough it has already under gone its cleaning by pressure washer. the range of approach is 5F to 10F.

as what i know, the approach of the AHU should be normally ranging from 0 to 3F.

what could be the cause of this high AHU approach??
 
Replies continue below

Recommended for you

Another thing to consider is the coil face velocity.Too low values(say less than 2m/s) can make the flow laminar and reduce approach
 
the 0 to 3F is the standards as per AHSRAE... i havent seen the manufacturers specs because the building wasnt able to provide it to us.


it is chilled water, fin spacing is 2.12mm... the coil face velocity is 2m/s for air... right???
 
Coil face velocity is for air side.Tube velocity(water side) should not be less than 1.2m/s.Also check if coil piping connection is done in a counterflow pattern ie warm air first to make contact with warmer coil tubes
 
Status
Not open for further replies.
Back
Top