Rhonda2
Mechanical
- Dec 18, 2003
- 20
With conventional (pressure dependent) control valves installed at large cooling coils, what leaving air temperature (LAT) variation should be expected relative to setpoint in operation with modern controls? Does it vary depending on the location of the coil in the system?
We are seeing numerous situations where LAT varies significantly due to differential pressure variations across control valves. This leads to variation in chilled water flow and subsequently to variation in LAT.
When LAT falls below setpoint, reheat masks the problem but causes additional ton-hours to be consumed. When the LAT rises above setpoint, fans work harder to sustain comfort conditions and humidity issues may arise. Many facilities have raised the LAT setpoint in operation because of inability to meet the original value.
I'd like to hear about some experiences in the field and what design options are being employed to address these concerns.
Thanks,
We are seeing numerous situations where LAT varies significantly due to differential pressure variations across control valves. This leads to variation in chilled water flow and subsequently to variation in LAT.
When LAT falls below setpoint, reheat masks the problem but causes additional ton-hours to be consumed. When the LAT rises above setpoint, fans work harder to sustain comfort conditions and humidity issues may arise. Many facilities have raised the LAT setpoint in operation because of inability to meet the original value.
I'd like to hear about some experiences in the field and what design options are being employed to address these concerns.