Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Air Conditioning

Status
Not open for further replies.

nastran2002

Mechanical
Nov 22, 2002
7
Hello,

I may have to put together a air cooling system. One option is to blow air on a finned tube like an evaporator. My question is what if I do not have enough heat in the air to evaporate all the refrigerent? How is this done in standard a/c applications? Are there heaters or expansion tanks used to make sure that only gaseous refrigerent goes into the compressor?

Thanks
 
Replies continue below

Recommended for you

they are called superheaters. You restrict the flow through things like: recycles, lower suction pressures.
 
In "standard" a/c the refrigerant flow is metered - typically with a thermal expansion valve - to maintain some level of super-heat leaving the evaporator.

The suction pressure is often monitored, and the compressor will either unload, or shut-off when it drops to low.

Some systems will incorporate a suction accumulator to prevent liquid from reaching the compressor under unusual operating conditions.

Some systems will incorporate a suction/discharge heat exchanger.
 
If the load is say less then 5 tons you may want to install a variable speed scroll compressor. this will adapt to a variable load better then a compressor with unloading. estimate the prejected load as close as possible
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor