Air Content in residential concrete 1

fp23

Structural
Aug 2, 2024
20
What do you all call out for air content in residential concrete? Specifically foundation walls and footings. I've been revamping my general notes and have seen other engineers specify no air, 5-6%, or not mention it at all. No air seems to be the most common.

Based on the ACI I'm coming to the conclusion that footings and foundation walls should both be F1 at a minimum (maybe F2 for some foundation walls) and should have 5% air, although this feels a little conservative for the footings since they are at frost depth and the top of them probably won't see much freezing/thawing and/or water. Just curious if any of you have had pushback on this in the residential world.
 
Replies continue below

Recommended for you

For Canadians, this is all spelled out via our performance classes (cut sheet). Might be useful as a guide for you. Also, one thing that's often overlooked is the construction cycle. While some items may not require an air entraining agent due to limited freeze-thaw exposure, during service, quite often footings / slabs / walls and the like go through a construction cycle that has them exposed to the winter elements. In which case, an air entraining agent may be a good idea.

1740148634202.png

1740148431155.png

1740148447618.png
 

Attachments

  • 1740148615713.png
    1740148615713.png
    33.9 KB · Views: 0
Honestly, I rarely call out concrete strength or mix in residential.
I let the IRC handle it unless i actually need more strength.
Other than for strength, if I call out a mix, I am opening myself up to liability as I would appear as an "expert" in concrete mix design - which I am not.
 
Thanks all, helpful to get some other opinions. I think I'm going to leave it on there and see if I get pushback from anyone. Like TRAK said, i'm guessing that residential concrete subs are just going to keep using whatever mix they always do.
 
I generated this from the durability requirements in ACI 318 and 332. Be sure to check it for accuracy before you use it. I delete lines that don't apply to the project, and edit if needed for additional strength or other performance requirements.

1740159177257.png
 
Are you located in a cold environment with a frost line? The air entrainment is more important if you are worrying about freezing temps.
 
I have the standard notes on my drawing per what ACI says. Like mentioned above, no one reads them.

Except for recently I had a homeowner GC that actually read them and asked for me to review the mix design. The local residential concrete supplier literally didn't have a mix to provide.
 
Last edited:
4,000 for footings, Pham? That seems like a bit much. I suppose it will be 2,500 after they add the on-site water :)
I'm in the swamp. All footings are in contact with water around here. W1 requires a minimum f'c of 4,000psi.
 
i'm guessing that residential concrete subs are just going to keep using whatever mix they always do.
That's a bad idea in these environs... You need the entrained air for freeze-thaw cycles.
 
I generated this from the durability requirements in ACI 318 and 332. Be sure to check it for accuracy before you use it. I delete lines that don't apply to the project, and edit if needed for additional strength or other performance requirements.

View attachment 5275
Thanks pham. Why do you use 6% air for F1?
 
Because it's the 'standard' (note other responses, above), and I'd rather have more than less, even with larger aggregate sizes. If the plant doesn't have a mix design that will work and they want to justify lower air entrainment because they larger aggregate, they can submit an RFI.
 