I'm getting into training for slab on grade design, and I had a question for my instructor that he wasn't able to answer.
I recall an instance where the engineer for the structural floor in our new office building (part office, part shop) specified 5-8% air entrainment. To the best of my understanding, the air entrainment was specified per CSA A23.1-09 requirements as we had specified the shop may not always be heated (we're in Canada). The floor was steel trowel finished and a chain drag test sounds delaminations over 20 to 30% of the floor area in the shop and office. Air entrainment tests showed just over 6%. For the office we had planned on polishing the concrete and leaving it, but we decided to tile the floor as we feared surface defects would "pop up" in the future. The shop was left as is and two years later we don't have visible surface defects (it's been heated continuously).
I understand naturally air entrained concrete tests around 2-3%, and steel troweled finishes on naturally air entrained don't typically make for delaminations. Some confirmation or further guidance is welcome here.
I also understand that air entrained concrete (4-8% per Table 4 of CSA A23.1-09) is required for concrete subject to freezing and thawing. So, my questions are as follows:
1) Was the engineer for the floor unlucky or is that a clear error to specify high air entrained concrete and a steel trowel finish? (the GC sure didn't think much of it)
2) What sort of surface finish should be specified for an interior slab that "could" be exposed to freeze thaw?
3) What sort of surface finish should be specified for an exterior slab that will clearly be exposed to freeze thaw?
4) If it needs to be a steel finish (for an interior slab) then is the lesser of the two evils to specify less air entrainment or natural air entrainment?
5) Is there a standard of practice that defines answers to these questions?
I recall an instance where the engineer for the structural floor in our new office building (part office, part shop) specified 5-8% air entrainment. To the best of my understanding, the air entrainment was specified per CSA A23.1-09 requirements as we had specified the shop may not always be heated (we're in Canada). The floor was steel trowel finished and a chain drag test sounds delaminations over 20 to 30% of the floor area in the shop and office. Air entrainment tests showed just over 6%. For the office we had planned on polishing the concrete and leaving it, but we decided to tile the floor as we feared surface defects would "pop up" in the future. The shop was left as is and two years later we don't have visible surface defects (it's been heated continuously).
I understand naturally air entrained concrete tests around 2-3%, and steel troweled finishes on naturally air entrained don't typically make for delaminations. Some confirmation or further guidance is welcome here.
I also understand that air entrained concrete (4-8% per Table 4 of CSA A23.1-09) is required for concrete subject to freezing and thawing. So, my questions are as follows:
1) Was the engineer for the floor unlucky or is that a clear error to specify high air entrained concrete and a steel trowel finish? (the GC sure didn't think much of it)
2) What sort of surface finish should be specified for an interior slab that "could" be exposed to freeze thaw?
3) What sort of surface finish should be specified for an exterior slab that will clearly be exposed to freeze thaw?
4) If it needs to be a steel finish (for an interior slab) then is the lesser of the two evils to specify less air entrainment or natural air entrainment?
5) Is there a standard of practice that defines answers to these questions?