This is great but it’s academia. We can get a 55°F leaving dew point by limiting DAT to 55°F; or a 51°F leaving dew point via a DAT of 51°F. If you want to get technical, the 55°F LAT with a larger cooling coil bypass factor will have a lower dew point. So you can have a lower coil ADP temperature with less fins per inch and have a 55°F LAT with a 51°F dew point, or a higher coil ADP temperature with more fins per inch and have a 55°F LAT with a 54°F dew point.
To me, this is minutia. As a general rule, if you need a space (e.g., pharmacy or OR) that wants a 68°F indoor temperature and less than 55% RH (dew point of 51°F), supply 52°F air during the summer and reheat the air to the desired room condition. The supply air temperature is the key; the fins per inch, bypass factor and other parameters matter, but are generally academic.
Wait, I might've answered the wrong question again... Sorry, I like going off on tangents.