Laundry room with 6 dryers that exhaust to outside.
RTU supplies into room.
OA is modulated up as dryers come on.
Room pressure sensor is used to control the OA damper.
Pressure sensor to maintain 0.05" setpoint (adjustable) in room.
Is this the best way to control?
Current sensors on the dryers will make controls complicated, not designing for this.
Is setpoint of 0.05" good for this setting.
Will opening of door to laundry by users make controls difficult?
Need to maintain pressure in space as the door to the laundry in fire rated and has to stay shut when needed and open easily when needed. Pressure cannot be excessive in room.
What is best location to install the pressure sensor?
RTU supplies into room.
OA is modulated up as dryers come on.
Room pressure sensor is used to control the OA damper.
Pressure sensor to maintain 0.05" setpoint (adjustable) in room.
Is this the best way to control?
Current sensors on the dryers will make controls complicated, not designing for this.
Is setpoint of 0.05" good for this setting.
Will opening of door to laundry by users make controls difficult?
Need to maintain pressure in space as the door to the laundry in fire rated and has to stay shut when needed and open easily when needed. Pressure cannot be excessive in room.
What is best location to install the pressure sensor?