I posed the question to the nfpa and got an official response to the question:
After consulting with Ralph Transue, the former Chair of the Technical Committee on Telecommunications, I have an answer for you:
The reason that NFPA 76 requires automatic detection systems with better performance than the minimum that NFPA 72 permits is the goal of telecommunications service continuity by protecting network equipment and cables.
a. The prescriptive approach of NFPA 76 chapter 6 achieves equipment protection by
i. Fire resistive equipment
ii. Very early warning fire detection
iii. Rigorous alarm response
iv. Manual intervention
b. Chapter 6 does not require automatic fire suppression provided that the telecommunications equipment is fire resistive.
c. Alternatively, NFPA 75 does require automatic fire suppression and NFPA 76 also requires automatic fire suppression if the equipment being protected is not fire resistive.
d. Therefore, because NFPA 76 chapter 6 relies upon manual intervention initiated by very early warning detection and rigorous alarm response, it is vital that the very early warning detection system operates very early.
Bell Core, AT&T and Bell Canada ran several full-scale tests of detection systems for the purpose of minimizing damage to telecommunications equipment to maintain service continuity. The requirements in chapter 8 (the tool box chapter) of NFPA 76 for very early warning detection performance is based on the results of the full-scale testing. The technical committee could not merely refer to NFPA 72 for very early warning detection systems because NFPA 72 compliant systems do not achieve the performance required.
If you need anything else regarding this, please feel free to contact me.
Please note the authority having jurisdiction determines compliance with the Code.
This response does not represent a Formal Interpretation as noted below.
Timothy A. Hawthorne
Fire Protection Specialist
NFPA – Quincy, MA USA
IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide professional consultation or services.