dfsmith
Electrical
- Jan 25, 2004
- 2
I have a runway lighting circuit that is currently inop.
It is powered by a 10kw 6.6a constant current power supply,which tests o.k.I have tested both output wires to ground and do have a high resistance path. I also have tested across the output wires at the CCR and have a very high restance path[32k ohms].I believe I have a damaged wire that is going to ground. My question are:
1- What are the most common reasons for series circuit failure.
2-What value resistance should I expect to see at the CCR end of the circuit. The wire length is approx 8k ft, and there are about 80 transformers in the loop.
3-Are there any "best way" troubleshooting techniques I should try.
One other factor to consider is the fact that almost all of the transformers are currently buried in 18 in of frozen New Hampshire ground and the current outside temp is -5F.
I do believe I have isolated the bad wire, but as yet havent jumped it out.
Iwould be greatful for any advice or guidence with this problem.
Thanks
Dave
It is powered by a 10kw 6.6a constant current power supply,which tests o.k.I have tested both output wires to ground and do have a high resistance path. I also have tested across the output wires at the CCR and have a very high restance path[32k ohms].I believe I have a damaged wire that is going to ground. My question are:
1- What are the most common reasons for series circuit failure.
2-What value resistance should I expect to see at the CCR end of the circuit. The wire length is approx 8k ft, and there are about 80 transformers in the loop.
3-Are there any "best way" troubleshooting techniques I should try.
One other factor to consider is the fact that almost all of the transformers are currently buried in 18 in of frozen New Hampshire ground and the current outside temp is -5F.
I do believe I have isolated the bad wire, but as yet havent jumped it out.
Iwould be greatful for any advice or guidence with this problem.
Thanks
Dave