Through past work by Yura the AISC specification has added appendix 6 which provides requirements for bracing.
Section 6.3 is for beams and includes both relative and nodal bracing requirements. The general concept I understand but we've been trying to understand the explicit application of this section to brace designs.
The main issue is that the brace strength equations ((A-6-5 and A-6-7) provide values for required brace strength, Pbr. This is given as a force in pounds as a function of bending moment and beam depth (ho).
But if we provide braces at 4 feet on center, we get a Pbr value. If we put braces at 8 feet on center we still get a similar Pbr value since the moment is the same. The beam might be a bit deeper since Lb would be larger, but that means that the brace force actually gets smaller since ho is in the denominator....and that seems counter-intuitive...fewer braces means less brace strength required.
Anyone have any views on this?
Section 6.3 is for beams and includes both relative and nodal bracing requirements. The general concept I understand but we've been trying to understand the explicit application of this section to brace designs.
The main issue is that the brace strength equations ((A-6-5 and A-6-7) provide values for required brace strength, Pbr. This is given as a force in pounds as a function of bending moment and beam depth (ho).
But if we provide braces at 4 feet on center, we get a Pbr value. If we put braces at 8 feet on center we still get a similar Pbr value since the moment is the same. The beam might be a bit deeper since Lb would be larger, but that means that the brace force actually gets smaller since ho is in the denominator....and that seems counter-intuitive...fewer braces means less brace strength required.
Anyone have any views on this?