Gopher13
Structural
- Jun 21, 2016
- 94
The organization I work for would like to build a pre-engineered metal building at one of our facilities. Up to now, I have never been involved in a PEMB project, but the way I understand it is I design the foundations (piers, foundation walls, footing) and the PEMB folks design everything above. I modeled a building frame to give me an idea of what the loads will be at the top of the piers. I also got preliminary loads from a local PEMB manufacturer to confirm what I modeled and their results are fairly close to mine. The controlling load case for lateral loads at the top of the piers is around 85 kips (LRFD), and the controlling load case for uplift is around 22 kips (LRFD). I am attempting to design the anchor bolts for these loads using ACI Appendix D and HILTI PROFIS software. Both methods produce similar results with concrete breakout strength of an anchor in shear controlling. We have nearly identical (same size, height, and bay spacing) buildings less than one mile from where this building is going to be located. These buildings have much smaller piers than what my design requires. Is ACI Appendix D not used to design PEMB anchors? The other more likely answer is I am doing something wrong, but I don't think so because I come close to matching HILTI PROFIS results. Has anyone encountered this problem before? Any tips? At this point, I am thinking of using a shear lug to take the lateral load.