Allen-Bradley SLC5/-4 and Panelview 1000

Status
Not open for further replies.

moltra

Electrical
Aug 14, 2003
15
I am designing a system with a SLC 5/04 processor which I will be connecting to a Panelview 1000 Via DH+. Connected to the RS-232 port will be a 22-SCM-232 serial converter that is connected to a Powerflex 4 and powerflex 70 drives.

What I need to know is, is there a way to connect to the SLC 5/04 via DH+ without disconnecting either the panelview or the serial converter.
 
Replies continue below

Recommended for you

To program using the other port. You need a 1784-PCM6/B cable and the 1784-PCMK. This will plug into the round port between 3 pin DH+ and the serial port.
 
Is the slc on a network?

If so you could put a drop line off of your main trunk line to connect to.
 